PROTECTION RELAY SYSTEM WhatsApp Chat with G18 schneider Relay conf

For joining our discussion groups: https://elec-engg.com/whatsapp-group-for-protection-engineers/ – I have set the under-voltage limit at 9.4kV (94kv, pt ratio 11,000/110, But relay trips at 9.47kV. what to do?– Make the vt connection vpp+vr. V peak to peak and v residual. In the configuration choose vpp+vr – can support and provide abb 230kv gis maintenance procedures.– I […]

PROTECTION RELAY SYSTEM WhatsApp Chat with G18 schneider Relay conf Read More »

PROTECTION RELAY SYSTEM WhatsApp Chat with Protection Engrs Grp

For joining our discussion groups: https://elec-engg.com/whatsapp-group-for-protection-engineers/ – Who knows the REF stability procedure? Both the voltage injecting method And the current injecting method?– When you create in the zone or out zone fault for REF stability there will always be a flow of current.– Short Primary Bushing Phase R S T with secondary terminal shorted

PROTECTION RELAY SYSTEM WhatsApp Chat with Protection Engrs Grp Read More »

PROTECTION RELAY SYSTEM STUDIES WhatsApp Group 10

For joining our discussion groups: https://elec-engg.com/whatsapp-group-for-protection-engineers/ – What are your configuration version and device firmware version?– If the error can not be reset it can be an indication of defective hardware even tho it is new. If you have changed any configuration Settings, try to upload the previous settings and check whether the error still exists

PROTECTION RELAY SYSTEM STUDIES WhatsApp Group 10 Read More »

PROTECTION RELAY SYSTEM STUDIES WhatsApp Group

Join the problem-solving WhatsApp group to get your answer: https://elec-engg.com/whatsapp-group-for-protection-engineers/ – There was a 5 MVA newly installed isolation transformer having ABB make REF615 relay connected to it.The problem was whenever the transformer was charged Relay SEF protection operated. When DR files were investigated, there was a huge unbalance current flowing during the charging of

PROTECTION RELAY SYSTEM STUDIES WhatsApp Group Read More »

WhatsApp & Telegram groups for Protection Engineers

To join our protection relay WhatsApp group, please send “interest” on WhatsApp: https://elec-engg.com/whatsapp-group-for-protection-engineers/ sample discussions – While I connect sip 5 bcu like that error I got. how can I solve that– Differential initial setting is 0.2*In?– What is the meaning of it? – Anybody has breaker dcrm result & procedure for testing breaker dcrm

WhatsApp & Telegram groups for Protection Engineers Read More »

WhatsApp & Telegram groups for Protection Engineers

To join our protection relay WhatsApp groups, please send “interest” on Whatsapp: https://elec-engg.com/whatsapp-group-for-protection-engineers/ Telegram:t.me/elec_engg Instagram:instagram.com/elec_engg WebsiteElec-Engg.comProtectionRelay.com Emailinfo@elec-engg.com protection relay 2 Discussion – During one phase PT failure, will overflux relay work? Has anyone seen this kind of voltage transformer connection?– Why is B-phase winding grounded on the secondary side?– Can u share the nameplate details